colinmono
Young Croc Joined: 10 October 2007 Location: Midlands UK Status: Offline Points: 1111 |
Post Options
Thanks(0)
Posted: 05 January 2018 at 9:55pm |
|
Just made up a 16a Ceeform plug > Permaplug 13a 4 way with 1.5mm H07 and it was a fairly snug fit into the cable entry on the Permaplug 4 way; I know 2.5mm would be preferable, will 2.5mm H07 really fit in there?
|
||
kedwardsleisure
Old Croc Joined: 20 January 2009 Location: Staffordshire Status: Offline Points: 4947 |
Post Options
Thanks(0)
|
|
I managed 2.5 into a 2-way 13A-use permaplug a few years ago. But that was to ensure compliant earth loop impedance on the run.
|
||
Kevin
North Staffordshire |
||
dylan-penguinmedia
Old Croc Joined: 14 April 2011 Location: Brighton Status: Offline Points: 4575 |
Post Options
Thanks(0)
|
|
It does fit, we have 80 x 16a T lines to 4 way Permaplugs with 2.5 H07, but like you say, it’s snug!
Edited by dylan-penguinmedia - 05 January 2018 at 11:04pm |
||
James Tengo
Old Croc Joined: 09 May 2008 Location: Brighton Status: Offline Points: 2155 |
Post Options
Thanks(0)
|
|
Ferrules are your friends in these situations
|
||
colinmono
Young Croc Joined: 10 October 2007 Location: Midlands UK Status: Offline Points: 1111 |
Post Options
Thanks(0)
|
|
Thanks.
Thanks James, I meant the flex entry to the body of the Permaplug 4 way looks tight for 2.5mm H07 - the terminals look like they will accept 2.5mm ok, but I'll use ferrules anyway.
|
||
csg
Old Croc Joined: 17 September 2007 Location: bedford Status: Offline Points: 6086 |
Post Options
Thanks(0)
|
|
we ferrule every mains connection, simply a better solution. however I was under the impression that stuffing cable larger than the connector was designed for was a PAT fail - and that 13A should be a maximum of 1.5mm ( and nominally 1.25mm).
Given that 1.5mm is more than adequate for 16A over a shortish distance what is the reason people feel the need to try and fit 2.5mm cable into 13A plugs and sockets?
|
||
“The fact is this is about identifying what we do best and finding more ways of doing less of it better”
|
||
colinmono
Young Croc Joined: 10 October 2007 Location: Midlands UK Status: Offline Points: 1111 |
Post Options
Thanks(0)
|
|
It's a 5m 16a ceeform plug to fused 13a 4 way socket. My first thought was to use 1.5mm then I trawled through a few discussions on the topic on here and most people seemed to have gone with 2.5mm cable so started to question myself. |
||
csg
Old Croc Joined: 17 September 2007 Location: bedford Status: Offline Points: 6086 |
Post Options
Thanks(1)
|
|
1.5mm would be perfectly adequate at 16A, if your socket is fused at 13A across all sockets, then 1.25mm would be adequate!
|
||
“The fact is this is about identifying what we do best and finding more ways of doing less of it better”
|
||
imageoven
Old Croc Joined: 28 March 2007 Location: Scotland Status: Offline Points: 2186 |
Post Options
Thanks(0)
|
|
My preferred set up would be:
5m long 16A cable on 2.5mm 16A to fused 13A 4way on short 1.5mm More versatile, avoids a 5m coil of cable when your 16A supply is near |
||
Keep pushing on, things are gonna get better.
|
||
colinmono
Young Croc Joined: 10 October 2007 Location: Midlands UK Status: Offline Points: 1111 |
Post Options
Thanks(0)
|
|
Sounds good for general purpose cables. This cable is for a specific home use purpose (outside power for working in the yard), so extra connections would be overcomplicating things I think.
Edited by colinmono - 06 January 2018 at 12:36pm |
||
imageoven
Old Croc Joined: 28 March 2007 Location: Scotland Status: Offline Points: 2186 |
Post Options
Thanks(0)
|
|
I don't really like the 16A to 13A four way at all though (4 way will be marked 'max supply 13A' so technically a PAT fail)
I stock the single 16 to single 13A adapters and these http://www.rubberbox.co.uk/16A-supply/RUBSSP16413 |
||
Keep pushing on, things are gonna get better.
|
||
imageoven
Old Croc Joined: 28 March 2007 Location: Scotland Status: Offline Points: 2186 |
Post Options
Thanks(0)
|
|
These are the adapter I prefer
https://goo.gl/images/6ZNKmH One of these at the wall socket, Standard 13a four way extension cable. 30mARCD at wall if there isn't one over the 16A supply already |
||
Keep pushing on, things are gonna get better.
|
||