Two pair sub cable.
|
|||
odc04r
Old Croc Joined: 12 July 2006 Location: Sarfampton Status: Offline Points: 5482 |
Post Options
Thanks(0)
|
||
Oh no, not H07 per se. I was commenting solely on the current capacity of a 4mm cable.
|
|||
odc04r
Old Croc Joined: 12 July 2006 Location: Sarfampton Status: Offline Points: 5482 |
Post Options
Thanks(0)
|
||
But y'know, original quesiton was pretty open ended. I agree with other points, 4mm can take 32A reasonably safely in some cases, but they do tend towards the marginal side. By the time you have factored in the possibility ofchaining cables and covering large distances you'd be daft not to go 6mm. I'd use 4mm for short non-chained 1-2m runs e.g between distro and racks without worry.
|
|||
MattStolton
Old Croc Joined: 04 September 2010 Location: Walthamstow Status: Offline Points: 4234 |
Post Options
Thanks(0)
|
||
OK, missed your generalisation, which now makes sense. 4mm tends to conduct only just enough to supply 32A. Looking at Appendix 4, and the tables 4D1A etc for Copper conductors, without applying any derating factors, plenty of examples of under 32A capacities. MICA ("pyro") is the only real exception, the copper sheath obviously radiates heat away well to allow the conductors to glow, although it does mention ambient of 30degC, but Sheath operating temperature of 105degC!! |
|||
Matt Stolton - Technical Director (!!!) - Wilding Sound Ltd
"Sparkius metiretur vestra" - "Meter Your Mains" |
|||
MattStolton
Old Croc Joined: 04 September 2010 Location: Walthamstow Status: Offline Points: 4234 |
Post Options
Thanks(0)
|
||
Got my BS7909 out now, and cross referencing it to BS7671.
If it is a 60decC, use BS7671 table 4F1A. If 90degC, use BS7671 4F2A. If three phase in one outer sheath (i.e. 5 core), 4mm cannot supply 32A without getting too hot. For single phase, only a 4mm2, IF 90degC rated, up to 18m maximum length, is possible, as rated at exactly 32A. However, if any derating factor is applied, it will drop below 32A capacity, and a smaller supply fuse must be used. 60degC rated is not rated to carry 32A. |
|||
Matt Stolton - Technical Director (!!!) - Wilding Sound Ltd
"Sparkius metiretur vestra" - "Meter Your Mains" |
|||
Digbethdave
Registered User Joined: 16 November 2018 Status: Offline Points: 406 |
Post Options
Thanks(0)
|
||
With 3 core?
|
|||
odc04r
Old Croc Joined: 12 July 2006 Location: Sarfampton Status: Offline Points: 5482 |
Post Options
Thanks(0)
|
||
Would say that sounds very logical and pretty much in line with what I expected. Ok for short runs in open air and that's about it. 90C rating is interesting, again makes sense. You'd have to really punish a cable to make use of that safety factor but then what else are regs for... |
|||
JonB67
Young Croc Joined: 22 April 2016 Location: UK Status: Offline Points: 1376 |
Post Options
Thanks(0)
|
||
You seem to have found a minor flaw in my suggestion.
|
|||
Digbethdave
Registered User Joined: 16 November 2018 Status: Offline Points: 406 |
Post Options
Thanks(0)
|
||
It happens. Be OK for sub links. Well some people run cable from amp to box. |
|||
Sonic the hedge
Registered User Joined: 12 May 2020 Status: Offline Points: 161 |
Post Options
Thanks(0)
|
||
Cable thermal ratings depend on the insulation, H07 is 90degC rated. Also that's the conductor temp so the outside of the cable won't be so hot obviously. Unlikely to need a derating factor for trailing cable unless you are planning in running a whole bunch together. The limiting factor with length is not the current capacity it's the volt drop and loop impedance. Both are ultimately dependent on the source, UK mains is pretty solid and well regulated, but building wiring also has to be considered. Since copper has a negative thermal coefficient (impedance increases with temperature) the actual load on the cable is what matters. I would suggest therefore for powering audio amplifiers, which is essentially an intermittent load (with transient peaks) 4mm will be fine for 32A (assuming a decent source), actually I have used it as such plenty times. But wouldn't recommend it for more continuous loads eg lighting.
Edited by Sonic the hedge - 23 July 2020 at 6:37pm |
|||
TMH Music
Young Croc Joined: 07 April 2011 Location: London Status: Offline Points: 637 |
Post Options
Thanks(0)
|
||
I’ve been looking into making some 16a cables of various lengths i.e 5,10,15 & 20m lengths, but can’t find 16a Cee connectors that accept cables bigger than 2.5mm CSA. Anyone able to point me in the right direction?
|
|||
Nothing is foolproof because fools are so ingenious
|
|||
GAZ.
Old Croc Joined: 16 January 2007 Location: Hertfordshire Status: Offline Points: 2433 |
Post Options
Thanks(0)
|
||
There isn’t any as far as I’m aware. Reason being is 2.5mm is good for 20 amps, which exceeds the rating of the connector anyway. As such there’s no reason to use anything bigger.
|
|||