RoadRunnersDust
Young Croc Joined: 03 December 2013 Location: United Kingdom Status: Offline Points: 563 |
Post Options
Thanks(0)
|
|||
That shouldn't be necessary, 16A for a 6-gang will be fine when you consider that a 16A MCB/RCBO/Etc. will bang out FAR quicker than any 13A Fuse would on a normal extension cable |
||||
James Tengo
Old Croc Joined: 09 May 2008 Location: Brighton Status: Offline Points: 2155 |
Post Options
Thanks(0)
|
|||
25m is not a long run. Given a full 16a load using 2.5mm you’d only see a 1.2% volt drop over that distance. If the load was 5a you’d only see a volt drop of 0.3%. If the load was 1a you’d see a volt drop of 0.07%. Better go up to 120mm powerlock and back down...
|
||||
Jack_The_Ripper
Registered User Joined: 04 March 2018 Status: Offline Points: 214 |
Post Options
Thanks(0)
|
|||
I've found the bits now on Amazon, i'll connect this to the wal socket :
Then connect this cable to it : Then connect that cable to this : Then i'll use this socket base : https://www.amazon.co.uk/Invero��-Switched-Extension-Indicator-Approved-White/dp/B06XJ8C22Y/ref=sr_1_3?ie=UTF8&qid=1545156585&sr=8-3&keywords=fused+6+gang And i'll take the standard cable off it and put on a short 10cm 1.5mm 3 core cable.
Edited by Jack_The_Ripper - 18 December 2018 at 6:19pm |
||||
fatfreddiescat
Young Croc Joined: 15 October 2010 Location: N.E.Wales Status: Offline Points: 1083 |
Post Options
Thanks(0)
|
|||
Calculated with what load may I ask? Just re read that, if he was only drawind 16 amps then ok, he is inteneding to draw less so not a problem, probs better off ditching the extension lead altogether, but if he intends to run the full rig then the bigger cable would be worthwhile. The main issue with long runs is not voltage drop but complying with safety standards re earth loop impedance.
Edited by fatfreddiescat - 18 December 2018 at 7:02pm |
||||
APW
Young Croc Joined: 13 November 2012 Location: Kent, UK Status: Offline Points: 1174 |
Post Options
Thanks(0)
|
|||
Beware; you should not use arctic blue cable outside for 'entertainment events' as it doesn’t comply with the regs (BS7909). H07RN-F is rubber (not PVC), tougher, it has thicker insulation and stands up better to abuse. Also rubber cable is nicer to coil than PVC, especially when the cable is cold. https://midas-uk.co.uk/do-you-prefer-rubber-or-plastic/ I know it’s common to see Artic blue but it isn’t the correct stuff. For the same price as the artic blue in your link you can get the HO7 cable in my last post. |
||||
Jack_The_Ripper
Registered User Joined: 04 March 2018 Status: Offline Points: 214 |
Post Options
Thanks(0)
|
|||
It'll never be used outside.
|
||||
James Tengo
Old Croc Joined: 09 May 2008 Location: Brighton Status: Offline Points: 2155 |
Post Options
Thanks(0)
|
|||
Voltage drop directly affects earth loop impedance though, the resistance of copper is changed by temperature, the volts are lost as cable heating. It’s all interconnected.
|
||||
RoadRunnersDust
Young Croc Joined: 03 December 2013 Location: United Kingdom Status: Offline Points: 563 |
Post Options
Thanks(0)
|
|||
Also, if you think there’s going to be Earth Loop concerns on a 25m run of 2.5mm^2 for a 16A circuit then you need to get back under the rock you’ve poked your head out from
|
||||
fatfreddiescat
Young Croc Joined: 15 October 2010 Location: N.E.Wales Status: Offline Points: 1083 |
Post Options
Thanks(0)
|
|||
Pretty much industry standard to use 32amp for a 25m run and 6mm2 for a 32amp cable, I wonder why? Possibly I am over cautious these day's, my mates daughter was electrocuted at a festival last summer when walking barefoot on metal roadway that had been laid over a ceeform connector, she was hospitalized and is lucky to still be with us.
|
||||
RoadRunnersDust
Young Croc Joined: 03 December 2013 Location: United Kingdom Status: Offline Points: 563 |
Post Options
Thanks(0)
|
|||
I’ve never heard such a crock of shite in my whole life Gross negligence and cut conductors has nothing to do with what we’re talking about either. Although the notion that a large lump of metal that is literally laid on the ground would come into contact with a live conductor and that someone’s foot would be the first viable path to ground presented to it is dubious at best. Given the fact she’s not dead would also point towards there being an RCD in the mix and even a 300mA device would bang out if it was trying to energise a load of trackway that was laid across the ground. Given that and the absolute poo you’ve already come out with, I’m calling bullshit
|
||||
James Tengo
Old Croc Joined: 09 May 2008 Location: Brighton Status: Offline Points: 2155 |
Post Options
Thanks(0)
|
|||
What industry is that then? Certainly not lighting, with power consumption dropping like a stone with the advent of led technology and more energy efficiencent light sources. The mega pointe at 440w is brighter than the bmfl at 1700w, not to mention about 20kg lighter. Bung 6 on a truss 30m from your racks and you can quite happily power them off a 1.5mm soca.
BS7909 isn’t just about inspection and testing, its about planning and designing too. Blanket statements are not what it’s about. |
||||
csg
Old Croc Joined: 17 September 2007 Location: bedford Status: Offline Points: 6086 |
Post Options
Thanks(0)
|
|||
i quite agree, no one is using 6mm for 25M 16A circuits under normal conditions. Blanket statements and blanket policies are more likely to cause accidents and incidents as you stop looking at the actual risks present which is far more dangerous than planning and designing a system correctly.
|
||||